I was bored the other day and e-mailed the IET advice line on thier view of cables run in cavities.
Here is thier answer:
Hi *****
I am required to preface my remarks by saying that I have no authority to interpret the requirements of BS 7671:2008, Requirements for Electrical Installations.
The interpretation of BS 7671 is one of the roles of the Joint BSI/IEE Committee JPEL/64. However, within that constraint, I hope you will find my comments helpful.
Cables should be chosen and installed taking into consideration the environmental factors present. If a cable is chosen to overcome the factors present within a cavity wall,or the future possibilities, then a cable designed or by design capable of with standing these factors can be used, although I would not recommend it and would consider it extremley bad practice and poor workmanship. The case for proper cable support must also be adressed, how would you clip or support a cable properly in a cavity?. The only cable system with remotely advantageous environmental characteristics , in my mind, would be MICC. However the supporting containment for this must be installed in accordance with the regulations.
In short, if you find a cable that can withstand the environmental influences , you would’nt be able to satisfy the regulations for the support of cables. To that end you can’t put cables in cavities , mainly because they can’t be supported adequatly.
Cables traversing the cavity (for outside lights and sockets for example, should theretically be suitable for the environment at that point or protected from it (possibly using an insulated conduit ).
The general answer is No you can’t , unless your thin enough to slide down the cavity and clip the cable( of the correct type and in this case I feel that is MICC) to the inside of the cavity.
I hope this helps
I hope these comments are usefull to you
Many Thanks
*******
Here is thier answer:
Hi *****
I am required to preface my remarks by saying that I have no authority to interpret the requirements of BS 7671:2008, Requirements for Electrical Installations.
The interpretation of BS 7671 is one of the roles of the Joint BSI/IEE Committee JPEL/64. However, within that constraint, I hope you will find my comments helpful.
Cables should be chosen and installed taking into consideration the environmental factors present. If a cable is chosen to overcome the factors present within a cavity wall,or the future possibilities, then a cable designed or by design capable of with standing these factors can be used, although I would not recommend it and would consider it extremley bad practice and poor workmanship. The case for proper cable support must also be adressed, how would you clip or support a cable properly in a cavity?. The only cable system with remotely advantageous environmental characteristics , in my mind, would be MICC. However the supporting containment for this must be installed in accordance with the regulations.
In short, if you find a cable that can withstand the environmental influences , you would’nt be able to satisfy the regulations for the support of cables. To that end you can’t put cables in cavities , mainly because they can’t be supported adequatly.
Cables traversing the cavity (for outside lights and sockets for example, should theretically be suitable for the environment at that point or protected from it (possibly using an insulated conduit ).
The general answer is No you can’t , unless your thin enough to slide down the cavity and clip the cable( of the correct type and in this case I feel that is MICC) to the inside of the cavity.
I hope this helps
I hope these comments are usefull to you
Many Thanks
*******