Hi its been a while since college and need some help with a calc.
I have been asked to put in a supply for a old spot welder ,The only info i have is
its 150 kva 2 phase .
I need help to calc amps
 
so on 2 phase that's 75kva per phase (approx. assuming load shared equally). assuming 230V per phase, that gives you 75K/230 = 326A per phase. !!! bloody big cable for that beast. but i can't see any welder being 150KVA. someone must have misread. 15KVA seems closer to the mark, and even that's a lot.
 
It might be worth involving someone with experience in this field.

A load like that turning on and off can cause all sorts of issues in the property.
From electric noise affecting radio and computer systems to motors and lighting being affected.

Also it may well have a huge inrush current so protection of circuit will need to be considered carefully.

If the site has pfc it could play havoc with the controller for that.
 
so on 2 phase that's 75kva per phase (approx. assuming load shared equally). assuming 230V per phase, that gives you 75K/230 = 326A per phase. !!! bloody big cable for that beast. but i can't see any welder being 150KVA. someone must have misread. 15KVA seems closer to the mark, and even that's a lot.

It's a spot welder, those things can get a lot bigger than 150KVA!
[automerge]1583399444[/automerge]
It might be worth involving someone with experience in this field.

A load like that turning on and off can cause all sorts of issues in the property.
From electric noise affecting radio and computer systems to motors and lighting being affected.

Also it may well have a huge inrush current so protection of circuit will need to be considered carefully.

If the site has pfc it could play havoc with the controller for that.

I know of one that was running on free electricity for about 6 months, the type of meter they had couldn't register the short pulses properly and so didn't record the power used.
 
It's single-phase 415 / 400V. It needs to be connected across two lines of a 3-phase supply to get 400V, hence the comment about it being '2-phase', but the unit itself is actually single-phase. Therefore 150k/400=375A. However, lower rated switchgear and circuits are often permissible because of the very short duty cycle.

As above, impulse loads can cause widespread disruption if not properly allowed for. The DNO have limits and requirements to ensure that they do not adversely affect other customers. Needs specialist advice before proceeding.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
sandy
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
ebs ltd

Thread Information

Title
calc help
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
john waters,
Last reply from
Lucien Nunes,
Replies
7
Views
1,450

Advert

Back
Top