I have been looking at this today and found it interesting so thought i would post a question for any of you to answer.

Calculate the neutral current on a lv 3 phase system.

L1 = 30Amps

L2 = 60Amps

L3 = 22Amps.
 
SQRT I²A + I²B + I²C - (IA x IB) - (IB x IC) - (IC x IA)

and if the answer is not 42, then i'm out. there's beer to be drunk. but a head guess is 24amps odd.
 
Last edited:
a rough guess ( and i mean rough) to check if you've don the calc. correctly ( i.e. not got way out) is to add the 3 line currents and divide by 3.
 
Or a little cheat I like is to use a line measurement representing L1 in cm, then draw a line representing L2 from the end point of line 1 at 120 degrees from line 1, then a third line representing L3 from the end point of line 2 at 120 again. The distance between the end point of line 3 and the start point of line 1 will represent the neutral current. It will look something like this:

[ElectriciansForums.net] Calculating Neutral current in unbalanced TP

p.s. Don't let your college lecturers see you doing this! lol
 
Or a little cheat I like is to use a line measurement representing L1 in cm, then draw a line representing L2 from the end point of line 1 at 120 degrees from line 1, then a third line representing L3 from the end point of line 2 at 120 again. The distance between the end point of line 3 and the start point of line 1 will represent the neutral current. It will look something like this:

View attachment 21606

p.s. Don't let your college lecturers see you doing this! lol

if you did it in inches, would the neutral current be 2.54 x as large? :rofl:
 
Could you explain this a bit more please. Do you mean where a neutral is not required?

As the previous poster hinted, things go haywire!!!
On an unbalanced star, if you lose the neutral, depending on the 3 loads, the star point wanders away from zero for starters!
I've got a link to an excellent book which will explain all.
You'll have to remind later though, too tired at the moment.
 

Reply to Calculating Neutral current in unbalanced TP in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top