Ive all ways for a bit of 2.5/1.5 Twin and Earth used this value 1.67 to calculate my R2 from my R1 values.
2.5/1.5= 1.66666666666666666667
so if i got my R1 as 0.34 i would expect my R2 to be 0.57
But the electrician i was working with disagreed with this and pulled out his onsite guide and said i should all ways be using the actual resistivity of the cable 12.10/7.41 = 1.63 meaning his calculated r2 would be 0.55
whose method is right?
2.5/1.5= 1.66666666666666666667
so if i got my R1 as 0.34 i would expect my R2 to be 0.57
But the electrician i was working with disagreed with this and pulled out his onsite guide and said i should all ways be using the actual resistivity of the cable 12.10/7.41 = 1.63 meaning his calculated r2 would be 0.55
whose method is right?