Hi,

With reference to BS 7671 on Page 128:

Using the mathmatic formula can anyone tell me how to punch in a calculator the workings out of the following:

When calculating the minimum cross-sectional area of a protective conductor, the following is available:

Fault current = 650A
Op time of protective device = 0.35s
Constant K for protective conductor material = 115

The selected size of the protective conductor should be????

How do i type in on calculator the formula as dont understand the little maths diagram on page 128 of BS7671.

Thanks
 
Hi,

With reference to BS 7671 on Page 128:

Using the mathmatic formula can anyone tell me how to punch in a calculator the workings out of the following:

When calculating the minimum cross-sectional area of a protective conductor, the following is available:

Fault current = 650A
Op time of protective device = 0.35s
Constant K for protective conductor material = 115

The selected size of the protective conductor should be????

How do i type in on calculator the formula as dont understand the little maths diagram on page 128 of BS7671.

Thanks


Are you doing this for college work?

If you are you need to show all your working out as the marks are not just for the answer, if the question has 5 marks then you will only get either a half or one mark for the answer.

All you need to do is Square the fault current multiply this answer by the time and then divide the resultant answer by k.

Then what ever the answer is you find the Square Root of this which will give you the minimum CSA.
 
Last edited:
With the method you have given I come up with:

0.077

I am obviously doing it wrong as the answer on a sample sheet for 17the edition is saying the protective conductor should be one of the following:

A) 2.5mm
B) 4.0mm
C) 6.0mm
D)10mm

The answer sheet says B) 4.0mm

How is the math worked out on that if I am coming up with 0.077

Chris
 
With the method you have given I come up with:

0.077

I am obviously doing it wrong as the answer on a sample sheet for 17the edition is saying the protective conductor should be one of the following:

A) 2.5mm
B) 4.0mm
C) 6.0mm
D)10mm

The answer sheet says B) 4.0mm

How is the math worked out on that if I am coming up with 0.077

Chris


I apologise it is fault current squared multiplied by time then this answer is square rooted with this divided by k
 
Last edited:
Hi Chris,

i just went through the equation to find the answer its very easy to mess this up ( it took me a couple of attemtps ) . you only square root the top part of the sum and then divide that answer by K.. try this way..


square root of ( fault current squared x disconnection time )

so

( 650 squared = 422500 x 0.35 = 147875 )


square root of 147875 = 384.54

Now Divide your answer by K

384.54 divided by 115 = 3.34 mm2

3.34mm2 is the minimum size of conductor allowed... so the closest size you can use is???

yep 4 mm2


hope that helps
 
Re Ian.Settle

Dont ask me to do it again lol.

Seriously thanks a lot.

I did manage to work it out myself but its great that you guys are on the ball with the replies and obviously confirmed that I was doing the right method in the end at least.

Thanks again all of you.

Chris
 
i did one now you do one
chris or anyone else
zs test on an oven cct gives 0.68 ohms the previous cpc continuity test gave (R1+R2) as 0.35 ohmns ambient temp at time of test was 25c (factor 0.98) and the cable is 70cpvc(factor1.2)
if max tabulated value of zs for the cct is 0.86
show by calculation wheather measured zs vaule is acceptable
 

Reply to Calculation help! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top