sheeni
When calculating the max earth fault loop impedance of a 3 phase MCCB that you use the nominal voltage ie in this case it is on a 60Hz system (120 / 208V ) and a 350A MCCB : therefore 208 / (350 x 10 (C type)) = 0.05 ohms
Therefore Zs is required to be equal or lower than this in order for the MCCB to disconnect in the correct time under fault condition??