P
Penance
Hi All,
Been away for a few weeks but now starting planning on a job.
I will be installing a sub main for a single room office area in a house extension.
The sub main will be run in SWA protected by a 63a MCB. The run is 7 meters to a CU that will have 3 circuits on RCBO's
Circuits are
1x 32a ring for office area
1 x 20a A3 radial for small kitchen area within office. Kitchen area is just a microwave and kettle.
1 x 6a lighting
So my calcs have been -
Max demand
((20 + 6)/0.4) + 32 = 42.4
installation method is clipped direct so Lt is 42.4
Calculated VD is 1.49 using 10mm XLPE SWA
Does this all look OK?