Been away for a few weeks but now starting planning on a job.

I will be installing a sub main for a single room office area in a house extension.

The sub main will be run in SWA protected by a 63a MCB. The run is 7 meters to a CU that will have 3 circuits on RCBO's
Circuits are
1x 32a ring for office area
1 x 20a A3 radial for small kitchen area within office. Kitchen area is just a microwave and kettle.
1 x 6a lighting

So my calcs have been -

Max demand
((20 + 6)/0.4) + 32 = 42.4
installation method is clipped direct so Lt is 42.4
Calculated VD is 1.49 using 10mm XLPE SWA

Does this all look OK?
 
Way over spec'ed. Office equipment will be minimal in terms of ampage. How many people are going to be there?

Even on the ring in a house you would rarely get anywhere near 32A, and if you did it would be there for a few minutes (whilst the kettle boiled).
 
3 maybe 4 people, mostly using laptops and desk top printers.

Do you mean the SWA is overspec?
Reason for it being armoured is that customer doesn't want office boss needing to access house if there's an rcd trip.
10mm cuz I'm old fashioned and can't get head round smaller for a sub main.
 
Laptops are small consumers or power, so are printers. No problem with using SWA if you don't want to protect it with an RCD, but I'm sure 6mm will be more than adequate with a 40A MCB, if the installation method permits, or even with a 32A MCB!
 

Reply to calculation sanity check please in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top