I have a checkbox (CCB1), it does the continuity and insulation checks BUT how do I do the Loop and RCD tests with the checkbox which does not have these facilities on?

I have read that you should have a dedicated circuit to do the loop and rcd tests.

Can someone please explain in more detail please?

Instructions not very clear so a walkthough guide would be most welcome.

Chris
 
Last edited by a moderator:
Just install a dedicated, non RCD protected socket next to your CU and label it for test purposes only. As long as you test it with a recently calibrated meter first to prove the readings then you can use it to prove your meter.

Need to double check readings with a calibrated tester at regular intervals though, make sure they havn't changed
 
Just install a dedicated, non RCD protected socket next to your CU and label it for test purposes only. As long as you test it with a recently calibrated meter first to prove the readings then you can use it to prove your meter.

Need to double check readings with a calibrated tester at regular intervals though, make sure they havn't changed


Hi Lenny,

How comes I have to use a Non RCD socket??

I thought it has to be a socket which is RCD protected?

Chris
 

Reply to Calibration Checkbox CCB1 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

Excellent :-) The case and leads are in good condition. Two live leads, one with a test button. Looks like ÂŁ30 well spent.
    • Like
Replies
3
Views
943
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
257

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top