Had a callout there to a shop. Outside lights tripping the main rcd. One of the son lamps was causing it. Replaced it and seems fine now. Done an ir test between live and neutral to earth and got a reading of >999. Bad set up cause if one circuit has a fault it takes out the whole shop not good when customers are in.
I have recommended putting rcbo's in. What are your thoughts? I have a system in place that notifies the customer of power cuts. He got a message at 4am this morning to notify him of a power cut. The system is good as there is freezers and fridges in the shop. However this doesn't solve the problem of the whole shop tripping!
 
How can a son lamp be causing an earth fault?

its more likely the control gear i would think

i had a similiar job where a whole farm all the out buildings and the farmers house was protected at scource by one 100ma rcd, no down stream devices at all

getting calls every month

only thing you can do is split up the circuits over more rcd devices or rcbos, or could you not put freezers etc on dedicated circuits with own rcd(if required) for a start

im only guessing here as you dont say much about the existing set up
 
Most RCBOs are single pole so if you get a N-E fault it will trip but wont disconnect the N causing your main rcd to trip and you are back to square 1.
A dedicated supply to the freezers etc or split circuits over another RCD as mentioned above is a good option
 
Most RCBOs are single pole so if you get a N-E fault it will trip but wont disconnect the N causing your main rcd to trip and you are back to square 1.
A dedicated supply to the freezers etc or split circuits over another RCD as mentioned above is a good option

He'd only need a main RCD if the RCBO's were for earth fault protection.
 
TT system done about 8 years ago in line with the 16th edition. 100mA rcd supplying a dis board and a sub main to another dis board which is protected by a 30mA rcd.
 
So how come when I replaced the old lamp with a new one, it cured the tripping of the rcd? Would there not be an imbalance between live and neutral if the control gear is trying to ignite the faulty lamp hence causing the rcd to trip?
 
It's possible that the high voltage developed when trying to strike the dead lamp is causing breakdown of some faulty insulation in the luminaire, e.g. in the ballast windings. With the new lamp that strikes easily, the peak voltage is lower and it doesn't flash over, and it also survived your IR test. Some types of control gear can cause high leakage currents while striking even withouta fault, not so much with sodium but if the RCD is already carrying some leakage the increased capacitive current from the ignition impulses might have just pushed it over the limit.
 

Reply to callout to shop in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
480

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top