Whilst looking at the supply intake at a house rented by my mate I noticed the Main earth which was clamped to the sheaf of the supply cable was disconnected, the service head is a TNCS, the main earth from each small 3036 CU goes to this head as well as the two main bonding conductors, curiosity got me so a did a Ze at the service head earth block and the line at the (unsealed!) henley block, Ze was 19.9ohms
I moved the earth probe over to the old TNS lead and hey presto a Ze reading of 0.25ohms:yes:, I stopped short of re connecting it
Did an engineer from the DNO attempt to convert to a PME but missed out the link in the head?, if so why convert when TNS had a good Ze.
My mate is contacting the DNO today?
Cheers
I moved the earth probe over to the old TNS lead and hey presto a Ze reading of 0.25ohms:yes:, I stopped short of re connecting it
Did an engineer from the DNO attempt to convert to a PME but missed out the link in the head?, if so why convert when TNS had a good Ze.
My mate is contacting the DNO today?