LlandrilloSpark

Whilst looking at the supply intake at a house rented by my mate I noticed the Main earth which was clamped to the sheaf of the supply cable was disconnected, the service head is a TNCS, the main earth from each small 3036 CU goes to this head as well as the two main bonding conductors, curiosity got me so a did a Ze at the service head earth block and the line at the (unsealed!) henley block, Ze was 19.9ohms

I moved the earth probe over to the old TNS lead and hey presto a Ze reading of 0.25ohms:yes:, I stopped short of re connecting it

Did an engineer from the DNO attempt to convert to a PME but missed out the link in the head?, if so why convert when TNS had a good Ze.

My mate is contacting the DNO today?

Cheers
 
Re: Can anybody think of a good reason for the DNO to disconnect TNS with Ze of 0.25o

did you get the 19.9 with bonding out of the equation. if not that reading could be from the services bonding and the tnc-s not connected , as you say. need dno to come and sort it out.
 
Re: Can anybody think of a good reason for the DNO to disconnect TNS with Ze of 0.25o

did you get the 19.9 with bonding out of the equation. if not that reading could be from the services bonding and the tnc-s not connected , as you say. need dno to come and sort it out.

I agree, there's no way the PME is connected with that reading.

Sometimes TN-S is disconnected on failing supply cables and street joints and PME offered as an alternative.
 
Re: Can anybody think of a good reason for the DNO to disconnect TNS with Ze of 0.25o

Thanks

Straight ze of 19.9 with bonding disconnected, house still has rubber two core feeding lights, I dont think the supply cable is original, forgot to mention that also performed zs on the downstairs ring and it was 21ohm again bonding in place, I'll have to come clean here!!, i crimped a 10mm eyelet on the end of the old TNS lead and screwed it to the earth block on the head......zs on ring 0.65ohm, put it all back as it was then got him to ring SP soon as, the house is 1894!
 

Reply to Can anybody think of a good reason for the DNO to disconnect TNS with Ze of 0.25ohms? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top