Hi all,
Would like some advice on the below. Context:
Rural French domestic installation
TT system
Earth rod is situated inside the property, buried in the concrete subfloor
Distribution transformer (overhead supply) is very close, on a pole approx 40 metres from the property
I did some 3 pole earth electrode tests today using my Megger 1741. The distance between the electrodes was approx 20-25metres. The two test electrodes were buried to around 25cm. The local soil is fairly light with a little clay and some gravel. It last rained yesterday but has been fairly dry past few weeks. There is no other bonding to gas or water.
I consistently measured around 6 Ohms. I haven't done much earth electrode testing but from what I've read that is very good. I suspect it could be due to multiple things:
I wonder what your thoughts are. Is there a way this could be artefact? If not, which things (that I've mentioned or not) are likely to have the biggest impact on the good readings?
Many thanks in advance!
Would like some advice on the below. Context:
Rural French domestic installation
TT system
Earth rod is situated inside the property, buried in the concrete subfloor
Distribution transformer (overhead supply) is very close, on a pole approx 40 metres from the property
I did some 3 pole earth electrode tests today using my Megger 1741. The distance between the electrodes was approx 20-25metres. The two test electrodes were buried to around 25cm. The local soil is fairly light with a little clay and some gravel. It last rained yesterday but has been fairly dry past few weeks. There is no other bonding to gas or water.
I consistently measured around 6 Ohms. I haven't done much earth electrode testing but from what I've read that is very good. I suspect it could be due to multiple things:
- Short distance to the distribution transformer
- Possibility that the earth rod is tied to the metal framework of the foundation (though if encased in concrete, is that effective?)
- Recent rain
I wonder what your thoughts are. Is there a way this could be artefact? If not, which things (that I've mentioned or not) are likely to have the biggest impact on the good readings?
Many thanks in advance!