I have private two wire overhead supply from a tncs pole and meter remote 8th mile away can make this tncs at house
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Can i make a over head supply tncs in the UK Electrical Forum area at ElectriciansForums.net
Are you qualified as your name implies?
Are you sure it is TNCS or PME. I take it is a secondary metered arrangement with the origin connected to the grid.
20ohm at the house 0.25 at the poleWhat is the earth electrode impedance at the moment?
20 ohms is okay. You are better off with TT at the house as long as you have a time delay Rcd main switch. Perhaps post a picture of the house panel & cable entry.20ohm at the house 0.25 at the pole
I'm not sure you can, unless you are a DNO, as I think the use of the TN-C section is covered by the ESQCR:
"8 (4) A consumer shall not combine the neutral and protective functions in a single conductor in his consumer’s installation"
Cheers thanksAs @Electro-tech says if you are worries about 30mA RCD having a single point of failure, you can use a 100mA delay RCD as an incomer, and either dual 30mA for final circuit protection or (ideally) RCBO that are neutral-switching such as the latest compact ones from Wylex/Crabtree/Fusebox.
Unfortunately I have no idea how private supply/BNO style arrangements are covered for this under ESQCR rules. hopefully someone with more knowledge will be along soon such as @Julie. or a few of the usual suspects such as @James or @UKMeterman , etc.Thanks can't get any help from supply authority as the supply from pole is privately owned