Can I power 2 x 3kw immersion heaters from a single 3 phase contactor? | on ElectriciansForums

Discuss Can I power 2 x 3kw immersion heaters from a single 3 phase contactor? in the DIY Electrical Advice area at ElectriciansForums.net

Joined
Jan 27, 2019
Messages
54
Reaction score
7
Location
Wick
Is it ok/advisable/legal to power 2 immersion heaters (both in the same cylinder) from a single 3-phase contactor?

I need to connec
 
As in, two single phase elements? If so then yes, subject to the overall design of the circuit being suitable for the loads and I'd strongly advise having separate protection for each after the contactor. The only 'technical' issue is that you'll have an unbalanced 3ph load because you'll only be using two of the lines.

If they're 3ph elements then same thing, just make sure that you have protection by a suitable 3p MCB after the contactor and before the element - you'll probably find this easiest by mounting the contactor and CPD's in a small DIN rail box all together.
 
Or are you talking about using a 3p device on a 1ph supply to just have one contactor not two??
 
Is it ok/advisable/legal to power 2 immersion heaters (both in the same cylinder) from a single 3-phase contactor?

I need to connect 2 immersion heaters and I have a redundant 3 phase timer-controlled contactor that would be ideal if I can use it. I know each heater would need its own fuse/DP switch, and I would need to run a neutral back to the panel.
 
Is the coil of the contactor 3 phase? I wouldn’t think so... possibly 230v single phase, could even be 24 or 12v dc... you need to check that.

as for the contactor... it’s just a switch... 3 pole, not 3 phase. But it’s capable of switching 3 phase 400v
 
As in, two single phase elements? If so then yes, subject to the overall design of the circuit being suitable for the loads and I'd strongly advise having separate protection for each after the contactor. The only 'technical' issue is that you'll have an unbalanced 3ph load because you'll only be using two of the lines.

If they're 3ph elements then same thing, just make sure that you have protection by a suitable 3p MCB after the contactor and before the element - you'll probably find this easiest by mounting the contactor and CPD's in a small DIN rail box all together.
As in, two single phase elements? If so then yes, subject to the overall design of the circuit being suitable for the loads and I'd strongly advise having separate protection for each after the contactor. The only 'technical' issue is that you'll have an unbalanced 3ph load because you'll only be using two of the lines.

If they're 3ph elements then same thing, just make sure that you have protection by a suitable 3p MCB after the contactor and before the element - you'll probably find this easiest by mounting the contactor and CPD's in a small DIN rail box all together.

Yep thanks for that. They are single phase 240v heaters. I was planning to run each via a DP switch and an mcb or fuse. Is a DP switch actually required or will a single pole MCB be OK?
 
As Littlespark said, you'll need to check your coil voltage on the contactor (which will also - somewhere - in the switching circuit need a protective device [if it's 230 then just piggy back off the protected main circuit feeding all this]) but a 1p MCB satisfies the requirements for isolation.

Making an assumption that this is 2 x 3kW elements then I'd suggest your feed cable is likely to need to be at least 6mm.

Also..... if this is domestic then it falls under Part P as you're creating a new supply circuit/s
 
Is the coil of the contactor 3 phase? I wouldn’t think so... possibly 230v single phase, could even be 24 or 12v dc... you need to check that.

as for the contactor... it’s just a switch... 3 pole, not 3 phase. But it’s capable of switching 3 phase 400v
Coil is 240v single phase
Yes I'm aware the contactor is just a switch - this one happens to be switching 3 phases and is already installed. I just wanted to make sure I wasn't breaching any regulations by repurposing it to switch 2 independent single phase loads as opposed to the 3 phase motor that was there before.
 
As Littlespark said, you'll need to check your coil voltage on the contactor (which will also - somewhere - in the switching circuit need a protective device [if it's 230 then just piggy back off the protected main circuit feeding all this]) but a 1p MCB satisfies the requirements for isolation.

Making an assumption that this is 2 x 3kW elements then I'd suggest your feed cable is likely to need to be at least 6mm.

Also..... if this is domestic then it falls under Part P as you're creating a new supply circuit/s
Thanks..... I think that covers it. The feed cable I think is an imperial size of MICC but it's definitely larger than 6mm and I won't need to mess with it - that's the reason I want to repurpose what's there rather than replace it which would be an absolute pain.
 

Reply to Can I power 2 x 3kw immersion heaters from a single 3 phase contactor? in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Article
This is an RSS feed of thread: Leaking cylinder around immersion heater Content of the thread: Hi. My hot water cylinder has a small leak. It's...
Replies
0
Views
229
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
197

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top