Hello

I’m going to install a hard wired 230v security camera, incorporating floodlights, outside and above garage door onto brick.

An exposed expanded metal lintel (that is hollow) runs across the garage door opening. Outside it has a decorative brick facing. The brick is not load bearing.

I intend to run the mains cable clipped direct to the wall until it meets the lintel at 90 degrees and then inside the lintel to the mid point where it will go through a hole in the brick.

The lintel is under 150mm from garage ceiling (prescribed zones) and cable/accessories will be placed compliant with prescribed zones.

I already understand about:
1. IP rating for lights/camera;
2. Fused spurs off ring main through FCU with 2.5 mm2 cable to FCU and 1.5mm2 thereafter; or
3. Separate circuit from 3amp FCU with 16amp rcd/mcb;
4. Absolutely no drilling of lintel.

My question is simply - can I run the cable inside the hollow lintel with no clips/conduit? If not, how to get cable to destination compliant with regs?

TIA
 
Hello

I’m going to install a hard wired 230v security camera, incorporating floodlights, outside and above garage door onto brick.

An exposed expanded metal lintel (that is hollow) runs across the garage door opening. Outside it has a decorative brick facing. The brick is not load bearing.

I intend to run the mains cable clipped direct to the wall until it meets the lintel at 90 degrees and then inside the lintel to the mid point where it will go through a hole in the brick.

The lintel is under 150mm from garage ceiling (prescribed zones) and cable/accessories will be placed compliant with prescribed zones.

I already understand about:
1. IP rating for lights/camera;
2. Fused spurs off ring main through FCU with 2.5 mm2 cable to FCU and 1.5mm2 thereafter; or
3. Separate circuit from 3amp FCU with 16amp rcd/mcb;
4. Absolutely no drilling of lintel.

My question is simply - can I run the cable inside the hollow lintel with no clips/conduit? If not, how to get cable to destination compliant with regs?

TIA
Sorry,

3. Should read: separate circuit from consumer unit with 16amp radial supply only to this lighting/camera…
 

Reply to Can I run mains cable inside hollow metal lintel? in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock