Can I use a 4mm T&E for a 7.5Kw shower? | Page 5 | on ElectriciansForums

Discuss Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

Based on a 240V, 7.5kw shower and a total length of 16M of 4MM2 cable and assuming cable resistance at 4.3mohm/M then my (rusty) calcs give a current flow of 30.975ohms and a shower output of 7.368kw and a voltage drop of 2.13V through the cable resulting in a cable heat loss of 65.94watts or 4.12watts/meter of cable.

So is 4MM2 suitable??.
Only if it keeps cool enough.

That is one of the 3 critical tests for cable choice:
  • Current carrying capacity (combinations of resistance, insulation temperature limit, ambient temperature, and thermal insulation "method")
  • Voltage drop (resistance and length)
  • Zs for Automatic Disconnection of Supply (resistance, length, protective device and supply impedance)
Should I don the Cardinal Ximénez outfit and summon Cardinal Fang now?
 
I love these convos you have to put every detail in about every product or operation. The science behind it or the physics, the calculations like you designing an electrical installation right from your phone.

If you put anything in laymans terms someone is quick to point out a fall or bite ?

Have fun guys another forum i wont be on again.

You lot are way better electricians...well done

I notice you've been back on the forum this evening. I knew you'd be back.

As I say, stick around - there's a lot of knowledge on here.
 
Only if it keeps cool enough.

That is one of the 3 critical tests for cable choice:
  • Current carrying capacity (combinations of resistance, insulation temperature limit, ambient temperature, and thermal insulation "method")
  • Voltage drop (resistance and length)
  • Zs for Automatic Disconnection of Supply (resistance, length, protective device and supply impedance)
Should I don the Cardinal Ximénez outfit and summon Cardinal Fang now?
Installation method and ambient temperature takes paramount for most normal fixed wiring applications as it dictates everything else...
 

Reply to Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for your time and opinion.
Replies
11
Views
1K
Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
338

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top