Can I use a 4mm T&E for a 7.5Kw shower? | on ElectriciansForums

Discuss Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

You rate the cable for the worst installation method with regard to its current carrying capacity, that would be the trunking. Being contained in trunking reduces its current carrying capacity to below that required for a 7.5kw shower.
 
It would also be false economy as you can be certain that someone will want to replace it with a higher rated unit in the future. For the length of run and cost why not use 10mm and perhaps a 9.5kW shower which will perform a lot better in the middle of winter when the incoming water is really cold.
 
The cable is installed in 3 metres of trunking, 3 metres clipped direct, and 5metres in the joist space with no insulation,
Sounds like a fairly easy run to replace the cable.
if you are going to put your name on the certificate, make sure that it is compliment otherwise it will always be a nagging doubt in your mind that some day it will come back and bite you.
 
It would also be false economy as you can be certain that someone will want to replace it with a higher rated unit in the future. For the length of run and cost why not use 10mm and perhaps a 9.5kW shower which will perform a lot better in the middle of winter when the incoming water is really cold.
water is not much colder in winter. 18" down in the ground temp. is fairly constant all year round. at about 10degrees.
 
Yeah I did think it should be a 6mm minimum but this was wired by somebody else so this cable was already in place, so should i have to say to the customer that the cable needs upgrading,
Thanks
I would personally recommend to the customer that the cable requires upgrading as it was incorrectly rated for the installation method in the first place. However, rather than a scaremongering approach, I would focus on the benefits such as the possibility of a larger rated shower unit, like Dave OCD suggested.
 
I would personally recommend to the customer that the cable requires upgrading as it was incorrectly rated for the installation method in the first place. However, rather than a scaremongering approach, I would focus on the benefits such as the possibility of a larger rated shower unit, like Dave OCD suggested.
Ok will do, thanks
 
It would also be false economy as you can be certain that someone will want to replace it with a higher rated unit in the future. For the length of run and cost why not use 10mm and perhaps a 9.5kW shower which will perform a lot better in the middle of winter when the incoming water is really cold.
7.5 seems low, don't come across any of that rating
Would be a bit cold in winter as you say
 
mostly mains fed, but round here the mains pressure is so low that if anyone flushes the bog, all the showers go cold.
My elderly parents live with me, both are very much retired but are keen gardeners. I can guarantee that the minute I get home from work and decide to take a shower they either go water the plants or start washing up... They are both at the house all day, but still chose to use the water right at the moment I take my shower!

This is the down side of mains fed boilers and showers!

They grew up with stored water systems, or rather the boiled water from a kettle on a stove to fill a tin bath once a week jobby, so never even consider me in the shower each day.
 
My elderly parents live with me, both are very much retired but are keen gardeners. I can guarantee that the minute I get home from work and decide to take a shower they either go water the plants or start washing up... They are both at the house all day, but still chose to use the water right at the moment I take my shower!

This is the down side of mains fed boilers and showers!

They grew up with stored water systems, or rather the boiled water from a kettle on a stove to fill a tin bath once a week jobby, so never even consider me in the shower each day.
so just have a shower at Xmas, whether you need one or not. outside water will be frozen.
 

Reply to Can I use a 4mm T&E for a 7.5Kw shower? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for your time and opinion.
Replies
11
Views
1K
Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
337

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top