someone said i cant use fine stranded cable underground in PVC conduit.
the "F" in HO5-VV-F stands for fine stranded.
I cant see any 17th ed regulation why it cant be used underground in PVC conduit. what do you think?
 
Last edited:
You probably can use this cable, given that the mechanical protection is adequate!! Not a cable i would use for a buried cable installation, SWA is far superior in this respect....
 
There is no actual regulation against using it, I think it is more looked on as bad practice, as the very method of pulling the cable through the ducting/conduit could put such a stress on individual strands as to snap them inside the insulation, and therefore reducing it\s current carrying capacity.
 
Personally i wouldn't be using PVC conduit underground, no matter what cable is in it. PVC conduit isn't made for it, I would imagine it offer zero protection against anything other than some one digging up weeds with a hand trowel.

Do it properly and select a method which is meant to be buried.
 
What is this cable to be used for?
Is it carrying signals (eg for an alarm) at elv, or is it an lv (230V) cable for supply of power to a remote device?

If elv or signal, then I guess you'd be ok doing as you describe.
If it's 230V then I'd agree that you should use swa.
 

Reply to can I use HO5-VV-F in PVC conduit underground? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You should have no problems with what you want but even if you install conduit the cable still needs to be UF cable which is approved for under...
Replies
1
Views
668
Went into an MCCB, terminated very nicely thank you very much, however it was just me doing some training with crimping. 'introducing extra point...
Replies
11
Views
634

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top