Can i use the steel? | Page 2 | on ElectriciansForums

Discuss Can i use the steel? in the Australia area at ElectriciansForums.net

J

Jas0n7

Hey Guys,

I'm wiring a warehouse at the moment. I have the mains panels in one corner of the building. out of the mccb panel i have bonded the structural steel with a 25mm earth, bolted, lugged, labled everything.

Now heres my question, all the services come in the other end of the warehouse. instead of running a 10mm earth from one end of the building to the other cant i bolt, lug and lable a 10mm cable to the steel near where the water comes into the building and then earth clamp it to the water main?

I'm 99% sure you are able to do this but i can't find it in the regs book anywhere?

Please help!
 
Paul, I think wirepuller was referring to the "Is it possible to give them their own earth rod?" part of your post, that would certainly not comply with the reg's and would introduce different potentials on metalwork along with the dangers that that would present.

The lightning protection system is risk management and I haven't seen a single documented case of injury while in contact with a tape, can you imagine the odds of it happening?

Thanks for the answer, its just that I've got to go out of the pub for a cig now and it was one of those silly thoughts. The rod idea, didn't think before opening my mouth so to say. Hope the regs I quoted were useful, I'll stick to what I know and stop asking stupid questions. (until next time) ps, dose an electric fence have a fuse?
 
Don't stop asking questions!

As for the lightning question, I think you'll have a far greater chance of death from the ciggy! :)
 

Reply to Can i use the steel? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
245
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
  • Question
Norcal - thanks, belatedly. 'Tis the season when I don't get anything done, even though this project is near the top of the list. Per your...
Replies
7
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top