Can I use this switch button to turn an AC/DC PSU on and off? | on ElectriciansForums
Discuss Can I use this switch button to turn an AC/DC PSU on and off? in the UK Electrical Forum area at ElectriciansForums.net
London
I would like to control a Power supply AC/DC connected to mains with an input of 230v (2.4A/115VAC; 1.2A/230VAC) and output 5v / 40A (200Watts). Can I use a switch button rated 3 A @ 250 V AC to turn it on and off? It would be one of these or something similar.
That looks like a momentary switch. You would need a latching one. I haven't checked the voltage/current ratings.
as above 40A (200watts) @ 5V is roughly 0.8A @240V. allowing for losses in the PSU , 1A is close to the mark. you'll need some fat cables on the 5V side though. 6.0mm?
Don't forget that SMPSUs can have high inrush that can weld switch contacts together. I would look for a switch with at least 3A inductive or 10A resistive load rating to ensure reliability.
That's ok then, the output current may be 40A, but the input current will not be. Remember, power is I x V and so the higher input voltage means less current.
Thank you! Yes indeed I was a bit confused as to which amount of current I was supposed to look at and provide a switch for. First time working with switches and AC.
No problem. Bear in mind Lucien's good advice about choosing a suitable current rating. Your switch will last longer then.
Thank you! This is really useful. The PSU will be powering 11 LED matrices, each potentially drawing up to 3A (though it will stay below that as I won't use full white colours)
Reply to Can I use this switch button to turn an AC/DC PSU on and off? in the UK Electrical Forum area at ElectriciansForums.net
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...