hi currently doing remedial works on a commercial office. I have a lighting circuit on a 6 amp mcb type B within a split load board covered by a 63amp 30ma Rcd . I have taken a zs reading of 750 ohms from a light which is too high . The existing installation is taking its earth from metal conduits embedded in the concrete ceiling.
My question is do I ignore the reading as there is a rcd in place or run a earth wire to the lights. The lights are metal Flaurecents ?