so currently doing my level 3 diploma and have this question I'm stuck on can anyone help?
a radial circuit is protected by 20A type B circuit breaker and is wired using 2.5mm2 70C thermoplastic single core live conductors with 1.5mm CPC to a length of 28mm in steel trunking. ambient temp is 20C supply is 230V single phase TNCS system. Ze & prospective fault current is recorded at 0.1 ohms and 2.3KA.
- already worded out R1 and R2 for the circuit which is 0.546.
- NEED to find - value of short circuit at end point of the circuit?
- AND will the circuit breaker disconnect within the required time under fault conditions.?
Cheers
a radial circuit is protected by 20A type B circuit breaker and is wired using 2.5mm2 70C thermoplastic single core live conductors with 1.5mm CPC to a length of 28mm in steel trunking. ambient temp is 20C supply is 230V single phase TNCS system. Ze & prospective fault current is recorded at 0.1 ohms and 2.3KA.