Discuss Can SWA be run in the same metal trunking as singles? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes, complete SWA. We have installed trunking for an installation with 2.5mm, 4mm and 6 mm singles.do you mean complete SWA? with the armour? or glanded into the trunking, and the inner cores within trunking?
"Singles" cable has a slightly tougher insulation than something like the inner basic insulation of t&e... Can take a bit of rough treatment no problem.
Thanks for the reply, the fault current will be 10Ka (theoretical maximum at origin) for the swa as we are right by the site intake.You are fine with that. Of course usual good installation practice needed, but SWA won't move that much unless you are looking at really high energy faults, and more so for sets of AWA singles making up a really high current 3P set.
Thank you! We have a massive amount of space left on the trunking. A maximum of 10% capacity before the 10mm SWA goes in.I can think of reasons why the clerk of works might not want SWA eating up space in trunking, but none that involve wiring regulations.
For some reason he doesn't like it clipped direct. Unfortunately it's at the beginning of a 70m run so glanding into trunk is not an option. Clerk also refuses to allow us to clip direct.Possible future plans require the space in the trunking?
Whats wrong with running the SWA alongside the trunking? Its mechanically protected already. Or, as i said earlier, gland it in and run it through without the armour.
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.Clerk of works will have the final say. I wouldn't waste time arguing with him and would instead ask how he'd like it to be routed - limitations with regard to support might actually result in him having a change of mind. Do whatever he wants and invoice accordingly.
He has refused to make suggestions on how to actually do it as he states 'that's not his job'.