M

mikejd

Hi I have two 6mm csa cables in the loft each going back to a separate 30A mcb in the CU. One is redundant, the other goes to a broken 8.5kW shower. I want to fit a new 9.5kW shower and would like to join both 6mm cables together at a 50A dpst shower switch, then run a short length of 10mm csa cable from the switch to the shower. Can anyone see a problem with doing this. Both 6mm cables are approx same length (12m), there is a RCD in the CU.
Thanks
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

I think you need to spell out your reasons for NOT doing this somewhat better. In power transmission this is normal practice! You ARE allowed to deviate from BS7671 provided the resultant safety is as good as compliance with BS7671 and you state you have deviated. The generic test docs are not compulsory. As I have said on this forum before, dual supply IS allowed. Every installation with solar panels has this as do auto start standby generators etc.
having said all that, I agree with all the statements that it is poor practice etc and certainly would not pass as a standard circuit.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thanks to you who have replied genuinely to my question, without feeling the need to result to sarcasm. No I am not a qualified electrician and never claimed to be but I am both a physics graduate and electronics engineer. I never doubted that regs would not allow this to be done, though from an electrical theory perspective it is perfectly feasible, Its a shame very few replies seemed to go beyond 'you cant do it as it breaks the regs' and considered the theoretical reasons why...of which there are few.
Thanks again

The "regs" are in place for a reason and part of that reason is to keep idiots safe from themselves.

You're very welcome to the advice.

Take care, goodnight and may your dog go with you.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

If the OP used a DP linked device it is plausible although not the norm in domestic ...


So to the regulars ...ill put a revamped version of the OP's question up... 2 x 6mm T&E short run clipped direct to a 10.5KW shower fed from a DP 25 amp mcb - trip interlocked - would it comply?

For arguments sake cable calcs all comply.
 
Last edited by a moderator:
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thanks to you who have replied genuinely to my question, without feeling the need to result to sarcasm. No I am not a qualified electrician and never claimed to be but I am both a physics graduate and electronics engineer. I never doubted that regs would not allow this to be done, though from an electrical theory perspective it is perfectly feasible, Its a shame very few replies seemed to go beyond 'you cant do it as it breaks the regs' and considered the theoretical reasons why...of which there are few.
Thanks again

Its not just that it is against regs.

If someone gets a shock in your house you will get reamed and go away for a long time.

If there is a fire I hope you can salvage some clothed because your insurance wont pay out
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

If the OP used a DP linked device it is plausible although not the norm in domestic ...


So to the regulars ...ill put a revamped version of the OP's question up... 2 x 6mm T&E short run clipped direct to a 10.5KW shower fed from a DP 25 amp mcb - trip interlocked - would it comply?

For arguments sake cable calcs all comply.

Not on that setup,as the OCPD would still be effectively SP, If I am following you correctly ? or two OCPD in parallel.

Edit: or did you mean 25A in total ?

Edit ii) Asuming you mean a true DP trip at 25A each, then Ha! I was wrong, reg 434.4 for fault protection only (conductors in parallel), but this comes with caveats that may not be suitable in domestic.

I don't think I have seen linked MCB's used in this way before (ACBs yes).

There are two types of DP MCBs that I am aware of, type one has two trip elements with linked trips and operating switch, used on two phase equipment, the other has a single trip element with the other pole being just a switch disconnector (linked as before), this type usually has one pole (the switch disconnector part) marked N for connection to the Neutral only.

I had to look it up though! it's late lol
 
Last edited:
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Not on that setup,as the OCPD would still be effectively SP, If I am following you correctly ? or two OCPD in parallel.

Edit: or did you mean 25A in total ?

Not exactly sure what you mean ?

DP means 25A each Still single pole but each live conductors into each pole, so by definition, are still dual circuits even if operation of one pole affects/trips the other...
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Edit ii) Asuming you mean a true DP trip at 25A each, then Ha! I was wrong, reg 434.4 for fault protection only (conductors in parallel), but this comes with caveats that may not be suitable in domestic.

I don't think I have seen linked MCB's used in this way before (ACBs yes).

There are two types of DP MCBs that I am aware of, type one has two trip elements with linked trips and operating switch, used on two phase equipment, the other has a single trip element with the other pole being just a switch disconnector (linked as before), this type usually has one pole (the switch disconnector part) marked N for connection to the Neutral only.

I had to look it up though! it's late lol

Yes I realised after, it is getting late lol, about time I was in bed.

I am sure DW eats the regs for breakfast lol

Reg 433.4 also mentions a single device for overload protection (conductors in parallel ), I suppose it is how you define a single device
 
Last edited:

Reply to can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top