I have a small camper. Input to the AC distribution panel normally comes from a 30A shore power source. I can also feed the distribution panel from an inverter powered by an LiFePO4 battery. The inverter output taps into the distribution panel on the same bus bars to which the shore power connects. Thus, it is possible that the camper could be supplied by shore power, and if the inverter were plugged in then both shore power and the inverter would be supplying power to the camper at the same time. That seems like it could potentially be an issue. Am I wrong? What would be the outcome if it were to happen? I'm thinking it would be good to install a manual transfer switch, so that it would be impossible for both shore power and inverter power to be connected to the distribution panel at the same time. But I won't bother if it is unnecessary. Please advise.
 
TL;DR
Is it an issue for an AC distribution panel to receive power from both an electrical company power line and an inverter line at the same time?
Connecting shore power to the inverter output is likely to destroy the inverter unless it is a grid connected inverter by design.

An inverter like this is designed to work in parallel with your shore power or when disconnected from shore power.

 
Connecting shore power to the inverter output is likely to destroy the inverter unless it is a grid connected inverter by design.

An inverter like this is designed to work in parallel with your shore power or when disconnected from shore power.

It is a Jackery Explorer 1000 v2. It has a UPS/pass through functionality, but only for a max of 15 amps input. With that limit, I cannot route 30A shore power through the unit. It seems like I'm correct that having both shore power and the inverter on the same circuit at the same time is an issue. I'll install a transfer switch, unless there is a better and/or easier solution suggested.
 
It is a Jackery Explorer 1000 v2. It has a UPS/pass through functionality, but only for a max of 15 amps input. With that limit, I cannot route 30A shore power through the unit. It seems like I'm correct that having both shore power and the inverter on the same circuit at the same time is an issue. I'll install a transfer switch, unless there is a better and/or easier solution suggested.
You should use a transfer switch, wired so that it disconnects the shore power cable when switched to inverter power, otherwise you could have hazardous voltage on the pins of the shore connector(s) when not plugged in!
 
You should use a transfer switch, wired so that it disconnects the shore power cable when switched to inverter power, otherwise you could have hazardous voltage on the pins of the shore connector(s) when not plugged in!
Thank you! I will add a manual transfer switch.

I was hoping that I'd be wrong and it wouldn't be an issue. Sigh. I guess I'll dig out the wire strippers. :)
 

Reply to Can two AC sources be merged? in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
The diagram looks okay to me, except I'm wondering if the neutral needs to be run through the transfer switch as well as the hot, in order to keep...
Replies
1
Views
226
I'm bad. I forgot that I made this post and I started another that is very closely related. In it I have drawn out a detailed wiring diagram...
    • Like
Replies
3
Views
390

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top