Hi All,
First just wanted to say I passed my domestic installer a couple of weeks ago, so a big thankyou to al those who gave me advice and helped me out when I was a bit puzzled. So again thankyou!
Anyways back to the post, got callled to a job yesterday where the landlord had told me the tenant had complained that the "low level sockets" in the kitchen had stopped working. Anyways turns out its the sockets that supply the dishwasher and fridge/freezer. The house has only one ring supplying all sockets (built in 2004, new builds for you!), then off this ring theyve put a three gang switch, which supplies them and the washing machine.
So plugged my socket tester in and everything seemed okay, plugged dishwasher in - everything okay. So done IR tests, rcd trip test, cont test - again, everything fine. Took the switch and sockets off, no dodgy connections or anything untoward.
I cant see the customer had made a mistake either because he told me he left it for 10 minutes and still nothing, so hes pulled the dishwasher and fridge out, connected above worktop and volla it worked.
Has anyone got any ideas what it could be?
The only fault I found was that the three gang switch was rated at 20AMP fed of the 32A ring. Maybe its getting a bit warm inside and theres a dodgy connection inside?! Oh and forgot to mention that the dishwasher AND fridge went off both at the same time, and theyre fed seperately from the switch.
Interesting to see a new build with a 10mm main earthing conductor on a PME aswell :hurray:
Regards,
Rob
First just wanted to say I passed my domestic installer a couple of weeks ago, so a big thankyou to al those who gave me advice and helped me out when I was a bit puzzled. So again thankyou!
Anyways back to the post, got callled to a job yesterday where the landlord had told me the tenant had complained that the "low level sockets" in the kitchen had stopped working. Anyways turns out its the sockets that supply the dishwasher and fridge/freezer. The house has only one ring supplying all sockets (built in 2004, new builds for you!), then off this ring theyve put a three gang switch, which supplies them and the washing machine.
So plugged my socket tester in and everything seemed okay, plugged dishwasher in - everything okay. So done IR tests, rcd trip test, cont test - again, everything fine. Took the switch and sockets off, no dodgy connections or anything untoward.
I cant see the customer had made a mistake either because he told me he left it for 10 minutes and still nothing, so hes pulled the dishwasher and fridge out, connected above worktop and volla it worked.
Has anyone got any ideas what it could be?
The only fault I found was that the three gang switch was rated at 20AMP fed of the 32A ring. Maybe its getting a bit warm inside and theres a dodgy connection inside?! Oh and forgot to mention that the dishwasher AND fridge went off both at the same time, and theyre fed seperately from the switch.
Interesting to see a new build with a 10mm main earthing conductor on a PME aswell :hurray:
Regards,
Rob