Just done a job connecting a fused spur on a ring to be used to supply a 2KW fire. When I came to do the testing (Minor Electrical Installation Work) I was unable to get the CU cover off. This was due to the customer fitting the kitchen cupboard tight up to the bottom of the CU and the ceiling slightly running down. I tested the ring from the socket and got figures for R!+R2, insulation values, ZS & RCD times. All were ok.
I checked the water bonding but could not see a direct bond on the gas only supplementary bonding across the central heating and gas pipe near the boiler.
How would you all fill in the form, detail this as a departure or just as comments.
Your comments would be appreciated.
I checked the water bonding but could not see a direct bond on the gas only supplementary bonding across the central heating and gas pipe near the boiler.
How would you all fill in the form, detail this as a departure or just as comments.
Your comments would be appreciated.