I have a car ramp that is powered from a single phase to 3 phase converter but the ramp struggles to lift anything other than very small cars. Is it possible that the converter is too small for the ramp motor? Here are the details i have on the motor and converter.
Converter:
Input : AC1PH 200-240v 50/60Hz 40A
Output : AC3PH 0-240v 0-400Hz 17.5A 6.7kVA
Motor:
Motor power : 4.kKW
Voltage : 230-400 V 3ph
Absorption : 230V:20.7A
400V:12.0A
Poles : 4
230 delta / 400 star
20.7A delta / 12A star
Thanks
Converter:
Input : AC1PH 200-240v 50/60Hz 40A
Output : AC3PH 0-240v 0-400Hz 17.5A 6.7kVA
Motor:
Motor power : 4.kKW
Voltage : 230-400 V 3ph
Absorption : 230V:20.7A
400V:12.0A
Poles : 4
230 delta / 400 star
20.7A delta / 12A star
Thanks