There is a difference of opinion in that a testing company carrying out an EICR has classed lack of RCD protection as a C2 where I understand this type of fault to be a C3 according to Guidance Notes 3 Table 3.5. Their opinion has been formed in reference to a publication called EICR Code Breakers as per the attachment. I had not heard of this book previously and have ordered a copy to see if there is something there I am unaware of but whilst I wait for delivery I thought I would throw it out there to see if anyone else has experience of this?
The building was erected early to mid nineties I would guess it came under 16th edition amendment 2. I am pretty sure it is mostly in galvanised and earthed conduit though I don't know every inch and therefore the reference to PVC/PVC may be correct in some instances. As far as I can see there are no high readings in the test certs that would mean the MCB protection is compromised.
Your thoughts appreciated
The building was erected early to mid nineties I would guess it came under 16th edition amendment 2. I am pretty sure it is mostly in galvanised and earthed conduit though I don't know every inch and therefore the reference to PVC/PVC may be correct in some instances. As far as I can see there are no high readings in the test certs that would mean the MCB protection is compromised.
Your thoughts appreciated