Did an EICR of a rented property, 2 up 2 down, old, one lighting circuit, cooker, ring and 2 radials (2 sockets in kitchenon one, hall socket on other).
All readings not to bad, not perfect I/R on kitchen radial, but damp walls so I wasn't surprised, end of line readings all good, realised that there must be loads of hidden joints on the lighting, so took readings at the furthest grond floor point and both ends of first floor.
Bonding up to date, but no RCD protection.
As rented recommended fitting RCD protection, gave landlord options and she went for a shiney new distribution board.
Came back, fitted it, retested all socket and cooker circuits and then got lazy..... as only the one lighting circuit checked the ground floor point I tested at last time as that had the highest reading last time and thoght jolly good, home time.
Silly me.
Two hours later called back when the tenant got home and tried to put the lights on upstairs - RCD trip!
After lots of hunting found a JB with the neutral and earth linked - AH HA I thought... - nope, take it out and no lights - upstairs missing the neutral - great, lifting boards and running a new feed 8pm at night with a moody tenant on my back.
Serves me right.
All readings not to bad, not perfect I/R on kitchen radial, but damp walls so I wasn't surprised, end of line readings all good, realised that there must be loads of hidden joints on the lighting, so took readings at the furthest grond floor point and both ends of first floor.
Bonding up to date, but no RCD protection.
As rented recommended fitting RCD protection, gave landlord options and she went for a shiney new distribution board.
Came back, fitted it, retested all socket and cooker circuits and then got lazy..... as only the one lighting circuit checked the ground floor point I tested at last time as that had the highest reading last time and thoght jolly good, home time.
Silly me.
Two hours later called back when the tenant got home and tried to put the lights on upstairs - RCD trip!
After lots of hunting found a JB with the neutral and earth linked - AH HA I thought... - nope, take it out and no lights - upstairs missing the neutral - great, lifting boards and running a new feed 8pm at night with a moody tenant on my back.
Serves me right.