Did an EICR of a rented property, 2 up 2 down, old, one lighting circuit, cooker, ring and 2 radials (2 sockets in kitchenon one, hall socket on other).
All readings not to bad, not perfect I/R on kitchen radial, but damp walls so I wasn't surprised, end of line readings all good, realised that there must be loads of hidden joints on the lighting, so took readings at the furthest grond floor point and both ends of first floor.
Bonding up to date, but no RCD protection.
As rented recommended fitting RCD protection, gave landlord options and she went for a shiney new distribution board.
Came back, fitted it, retested all socket and cooker circuits and then got lazy..... as only the one lighting circuit checked the ground floor point I tested at last time as that had the highest reading last time and thoght jolly good, home time.
Silly me.
Two hours later called back when the tenant got home and tried to put the lights on upstairs - RCD trip!
After lots of hunting found a JB with the neutral and earth linked - AH HA I thought... - nope, take it out and no lights - upstairs missing the neutral - great, lifting boards and running a new feed 8pm at night with a moody tenant on my back.
Serves me right.
:(
 
Like your drawing Anthony brag. Makes perfect sense, but...

In post one no mention of break in neutral. Just neutral and Earth connected.

In post 4 a bit more confusing, it says neutral was not connected where earth was linked. Not sure how to interpret that one.

Maybe wording not ideal.

Question to doomed, has anthonybragg got it right in his drawing. If so case cracked.
See post 7
 
Thanks for the drawing Anthony made things much clearer,I know I’m missing something here but why would the rcd only trip once the upstairs lights were switched?
When any switch is in the on position there would be Current through the residual current devices live, but no return feed through neutral as the return path would be via the cpc. I balance trip.

If all lights switched off no current through live and no current through neutral. Also non of the lights neutrals are actually connected to the neutral bar in the earth. No imbalance no trip.
 
Thanks Pete that makes sense, What’s confusing me is it only tripped with the upstairs lights when there is only a single lighting circuit? Not doubting anyone here just trying to keep up ha ha :)
 

Reply to Caught out by mt own lazyness..... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
693
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top