2.5 mm radial t&e supplying 2 twin sockets on 32a Rcbo. Code2?
6mm radial to heater three phase nny-j cable, ccp of 42a on 50a mcb code 2?
2.5 mm radial t&e supplying one ac unit 32a mcb code2?
The heater supply may be fine and not warrant any code.
If it is just a simple heater and is therefore a load which is not susceptible to overloading then overload protection is not required and cable calc can be done from Ib. The mcb will only be there for fault protection.
Reply to Ccp eicr code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Duh!!! Just re-read Op's original post, it was converted to a RFC!