H

Hawk

Can an MCB be used instead of an RCBO for a supply to a UPS centeral battery system if the required disconnection times are met?
 
If my memory serves me right, it is a 6kVA system that is installed. (by a different company)

Originally I was told by my boss that a 50A supply was needed to the comms room. I installed a 16mm cable protected by a 50A 30mA RCBO.

The engineer who installed the system has now requested that a 32A MCB be put in place of the RCBO as there will be a high earth leakage which may trip the 30mA RCBO.
 
Further thinking on this - if the earth current is over 30mA, what does the Designer say about the Installation? Surely there is a standard design for these installations?
Now that you know it could be over 10mA earth current, then you need to read 543.7.
 
The cable is run on tray above a suspended ceiling. It is a 16mm 3 core hi-tuf cable. Single phase. I haven't been speaking to the designer yet. Should see him on Monday.
 

Reply to centeral battery UPS system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
705
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top