Evening all. I have a question in the installation certificate. I am testing some sites around the country and on the certificate it needs the primary supply main fuse size and Ka type etc. All the sites these are sealed by supply authority so I have written 'sealed' on the certificate. Now I have been told that this is wrong and to put what the sticker says in the fuse holder. But surely any fuse could be fitted.

So guys and girls who is correct ??


many thanks all
 
Theoretically since you are not permitted to break the seal and actually check the fuse you should put not verified or LIM.
However if the head does have a label on it specifying the intended fuse size and type I tend to put "labelled as...."
 
Richard is spot on, never put it down as though you have removed fuse, I usually just put it down as a Limit, but Richard's idea is a good call.
 
Work on worse case scenario, and quote BS 88-3 100A fuse, 16.5kA breaking capacity, so your tails etc should be to this spec. If you are doing testing only on new installations, then this information should be available from whoever specced the supply. You can't LIM on an EIC, if you can't complete all the paperwork, then it is not complaint. If you can't find out from whoever specced it up, then contact the supplier, but they will only quotes what i have said anyway.

Cheers............Howard
 
Limitations are specifically for periodic inspections, not for use with EICs or MEWICs.
if you are unable to verify the fuse details by examination, you should contact the supplier, and use the information they provide.
 

Reply to Certificate query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
506
Don't worry about the 4A fuse, it's a Keston boiler, it'll be dead by the time you've found one and it's been delivered.
Replies
10
Views
981
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top