Having recently installed a submain, sheath to TN-C-S earth at supply end, isolated and TT'd at the far end I'm a bit unsure on the cert.

I have ticked both earthing types but am stuck on how to separate the values for each installation to put them on the same cert. Max Ze for example, should this be Ze from the meter, or Ze of the rod 100 metres away? We've done nothing whatsoever with the installation on the far side, just the distribution and provided an earth.

Common sense is telling me to write our cert just for the distribution cable up to the external board, as someone else is doing all that side and certing it separately. If they had installed the rod it would have been simple as it effectively falls on their side of the installation, but obviously we need to note the rod's Ze somewhere.

Anyone done a similar installation before and overcome this confusion? If so HELP I'M GOING CRAZY!!

Thanks :)
 
Yes indeed TT is to an outbuilding, and I have included the details of the rod and Ra in the particulars of installation at the origin as it's the only place to put them. As that figure (whether we class it as Ze or Zdb) is already noted, I'll put the Ze using the TN-C-S earth down under supply characteristics. It says to put the higher value down if more than one supply, but doesn't mention if one supply and more than one earth. That seems to make the most sense, even though the rod is from a sub dist board and not at the origin. Cheers :)
 
hi mate have you used two schedule of test results one for the supply which will have your origin tn-c-s Ze and the other schedule for the ccu in your outbuilding with the tt Zdb which is also the Zs for the the circuit from your distribution board supplying your ccu in outbuilding
you have 1 eic ,1 schedule of inspections and 2 schedule of test results 1 for each board
 

Reply to Certificating distribution circuit which is TN-C-S one end and TT the other? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top