Hi All,

Doing a full rewire on a terrace which also has to have 3 interconnected mains powered smoke detectors. I wanted to know if I include the smoke alarm circuit on the EIC as an extension to a lighting circuit, or as its a new wire just give it a dedicated supply from a 6A MCB and then include it on the certificate or issue a BS5389 cert aswell as the EIC or just include thesmoke alarms on a BS5389 cert and exlude them from the EIC? sorry for all the questions, I've searched the forum and this question seems to have been partly answered but just want water tight advice as I'm using the install for my ELECSA assesment. Cheers all
 
If you install the dectors on a lighting circuit then I would include the cabling of the fixed installtion on my EIC and do the tests.

If you supply them on a dedicated circuit again I would include it on the EIC as part of the fixed installation.

Before you commision the Detectors then I would do the test as per BS 58398-6

What type have you fitted grade D or E ?
 
one point you probably know anyway. if one of the detectors is in a kitchen, make sure it's a heat-rise, not smoke
 
Nice one, shall I still complete bs5389? Will elecsa rep want to see this?

Ask Elecsa bloke for a sample of the smoke alarm cert, he gave me mine, cos he picked it up on an EIC and told me i had to complete a seperate cert for the smokes.

cheers......Howard
 

Reply to Certifying Smoke Alarms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
282
  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top