My boss has set me a little bit of homework. A cable calculation I've found Ib,In,Iz Selected cable Ect. I now want to calculate the r1+r2 for x2 240mm2 swa cables in parallel using the swa as the CPC. I'm assuming the table in regs, giving the mV/A/m value, is not applicable when using the swa as the earth. any ideas ??
Thanks, I found a table values are in ohms per kilometre, so would I need to first convert these to milli ohms per meter then add the copper conductor and swa values together then this gives me the - milli ohm /m value
i find it easier to calculate R1 from the copper ( figures in osg ) and separately calculate the R2 from figures obtained for the armor. then add the two together.
I may be looking at the wrong table, but only goes to 50mm, the figure I found online was 0.0754 ohms per kilometre so would be only 0.019 ohms for my 260 meter run this seems really low even for a cable as large as 240mm, I got 0.124 over 260 meters for the r2 which seems realistic