davetherave1979

Have a customer who wants to swap the broken shower for a direct replacement same make load etc is this ok to change if there is no rcd or should I tell them that this must be fitted.
 
had a customer afew weeks back bought a 9.5kw shower that they wanted me to fit. Cable run ran within a plastered wall,then insulated (rock wool) stud work, across extra insulated loft (free insulation crew had been in), pull switch then back in loft to shower. Cable run was about 28metres so worked out 10mm t&e needed.......BUT manufacturers instructions stated for a run of 30metres 6.0mm was fine (no other info about diversity given).

Knowing it needed to be 10mm but instructions claiming 6.0mm is fine where does this manufacturer's stuff fit in with that????

After much conversation and having to prove calcs to customer (secondary school maths teacher of all things) eventualy agreed 10mm needed at extra expense.
 
Dont forget that the manufacture instructions are based on several different models.

a 6mm would be fine for any shower under 8.5kW.

I would still say have to be 10mm as a min for a 9.5kW shower - see your point though with the maths teacher
 
had a customer afew weeks back bought a 9.5kw shower that they wanted me to fit. Cable run ran within a plastered wall,then insulated (rock wool) stud work, across extra insulated loft (free insulation crew had been in), pull

Iswitch then back in loft to shower. Cable run was about 28metres so worked out 10mm t&e needed.......BUT manufacturers instructions stated for a run of 30metres 6.0mm was fine (no other info about diversity given).

Knowing it needed to be 10mm but instructions claiming 6.0mm is fine where does this manufacturer's stuff fit in with that????

After much conversation and having to prove calcs to customer (secondary school maths teacher of all things) eventualy agreed 10mm needed at extra expense.

In this situation i dont see how a manufacterer can specify 1 cable size is the same or adequate for all installations ? and at 28mtrs volt drop may be significant.
You did right , carry out your own assessment.
 

Reply to changing over shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top