Have a customer who wants to swap the broken shower for a direct replacement same make load etc is this ok to change if there is no rcd or should I tell them that this must be fitted.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss changing over shower in the UK Electrical Forum area at ElectriciansForums.net
If the manufacturers instructions say fit an rcd , then lose the instructions.
You guys need to think laterally ;-)
had a customer afew weeks back bought a 9.5kw shower that they wanted me to fit. Cable run ran within a plastered wall,then insulated (rock wool) stud work, across extra insulated loft (free insulation crew had been in), pull
Iswitch then back in loft to shower. Cable run was about 28metres so worked out 10mm t&e needed.......BUT manufacturers instructions stated for a run of 30metres 6.0mm was fine (no other info about diversity given).
Knowing it needed to be 10mm but instructions claiming 6.0mm is fine where does this manufacturer's stuff fit in with that????
After much conversation and having to prove calcs to customer (secondary school maths teacher of all things) eventualy agreed 10mm needed at extra expense.