So, a flat 6 floors and above needs an AFDD on each socket circuit. At up to ÂŁ150 each it is going to be an expensive undertaking if there are a number of socket circuits.
But! ... A 40A AFDD can be fitted in the CU. It can supply the socket circuits which will have their own DIN rail mounted fuses carriers fitted on the same DIN rail in the CU. The 40A AFDD is the master, the fused circuits slaves. Then fused circuits:
  • a kitchen (heavy appliances);
  • living room;
  • bedroom;
  • etc
All can have their own circuit, radial or ring, off their own fuse for over-current protection. Fuse are for selectivity conflicts with AFDD/RSCO/MCB's in series. But still have the protection of AFDD and RCD. Each fuse holder with a 4mm or 6mm conductors into the AFDDs terminal. The lights and and cooker can have their own RCBOs. In a typical flat that would be:

1) 40A AFDD;
1a) 32A fuse supplying kitchen sockets on ring final circuit;
1b) 20A fuse supplying sockets on the rest of the flat.
2) 40A RCBO supplying a cooker;
3) 6A RCBO for lighting.

Three circuits.
Two sub circuits.

Cost are now way down.
 
Last edited:
My personal take is you'd need to consider the possibility that you would become the designer of a type tested enclosure/assembly. I have a feeling that you would be using the AFDDs outside the bounds of their specifications which could open up a whole world of hurt if something went wrong.

The board would no doubt look amazing with all your hand crafted bodgery and you'd also be going against the regs as far as minimising inconvenience in the event of a fault, possibly to the point where (based on your circuit schedule) the flat would have no heating/hot water (I'm assuming it's gas, powered by 1b) due to a fault on 1a).

How easy is it going to be for people to fix a blown fuse (here I'm thinking specifically about availability of said fuses - you can't typically get these at B&Q or ScrewFix)?

To be fair, with the excessive faffing around you'd be doing in the consumer unit just to construct this solution, I think simply installing two appropriately sized AFDDs would work out to be a more economic solution once you factor in everything.

As much as I don't like the price, unfortunately they are now a requirement in specific situations, so get over it, pay the price and do the job properly... don't be a plank trying to use the letter of the regs to defeat the spirit of the regs.
 
The cost of the AFDDs are passed onto the customer and will eventually go down.
Trying to do it cheap now will end up being the same as when mainswitch RCDs came out with any number of mcbs coming off it.

Hence why certain regulations came in…. Eg, being left in the dark when you plugged in a faulty hoover
 
If its a flat and cost is critical then have one standard 32A RFC to rule them all from the AFDD, just route cable so kitchen stuff is very approx mid-way.

Cooker on RCBO radial without socket. Lights, etc, same as usual RCBOs.

Job done, nothing needing special design or certification as outwith "standard circuits".
 
As above over the next 2 or 3 years the unit cost of AFFDDDs will come down as sparks start buying more of them.
I remember when individual Rcbos were ÂŁ35-40 a pop now you can get them for a ÂŁ15
 
If its a flat and cost is critical then have one standard 32A RFC to rule them all from the AFDD, just route cable so kitchen stuff is very approx mid-way.

Cooker on RCBO radial without socket. Lights, etc, same as usual RCBOs.

Job done, nothing needing special design or certification as outwith "standard circuits".
One RFC can be done for sure. 4mm cable can be run to heavy current appliances in kitchen, to ensure a 2.5mm cable does not fry.

What I outlined in post 1 can be one 40A AFDD on a radial with two or three sub radials off it. There happens to be a fuse to the sub radials. The DIN fuse holders are in the CU for convenience. They can be outside in a separate enclose, but why when all can be in one enclosure. The CU.

Another angle is all the heavy appliances, say three of them, off a 6mm radial cable, with 2.5mm from 2nd to 3rd socket to reduce cable costs. One sub radial off the 6mm after AFDD serving other sockets, off their own fuse, say 25A. Fuse holder is in CU for convenience.
Lighting and cooker off their own RCBOs..
 
Last edited:
My personal take is you'd need to consider the possibility that you would become the designer of a type tested enclosure/assembly. I have a feeling that you would be using the AFDDs outside the bounds of their specifications which could open up a whole world of hurt if something went wrong.

The board would no doubt look amazing with all your hand crafted bodgery and you'd also be going against the regs as far as minimising inconvenience in the event of a fault, possibly to the point where (based on your circuit schedule) the flat would have no heating/hot water (I'm assuming it's gas, powered by 1b) due to a fault on 1a).

How easy is it going to be for people to fix a blown fuse (here I'm thinking specifically about availability of said fuses - you can't typically get these at B&Q or ScrewFix)?

To be fair, with the excessive faffing around you'd be doing in the consumer unit just to construct this solution, I think simply installing two appropriately sized AFDDs would work out to be a more economic solution once you factor in everything.

As much as I don't like the price, unfortunately they are now a requirement in specific situations, so get over it, pay the price and do the job properly... don't be a plank trying to use the letter of the regs to defeat the spirit of the regs.
The AFDD can serve a radial with sub radials off it. Within bounds of AFDD.

The sub radials just have fuses on them. Nothing wrong with that.

DIN fuse carriers in the CU is for convenience. A professional working in the CU would not bodge the job.
 
One RFC can be done for sure. 4mm cable can be run to heavy current appliances in kitchen, to ensure a 2.5mm cable does not fry.
Why do some people unnecessarily oversize cables as someone pointed out in another deceased thread
What I outlined in post 1 can be one 40A AFDD on a radial with two or three sub radials off it. There happens to be fuse to the sub radials.The DIN fuse holders are in the CU for convenience.
Why create unnecessary work the amount of time messing around and the material costs plus the added complications encountered if a fault occurs in the future you may as well just ............................................ install another AFDD and have done with it and bask in the long term savings
Another angle is all the heavy appliances, say three of them, off a 6mm radisl cable, with 2.5mm from 2nd to 3rd socket to reduce cable costs. One sub radial off the 6mm after AFDD serving other sockets, off their own fuse, say 25A. Fuse holder is in CU for convenience.
Lighting and cooker off their own RCBOs..
Why bodge an installation before it has even been used this is the sort of bodge you find after an installation has been in service for a decade or two not a new unused one
 
Thinking about it again, it is quite simple:
  • If they need more than one RFC due to electrical demand, then they can afford more than one AFDD.
  • If not, they can't afford to use those appliances!
Say a block of 60 flats in a 6 floor old block renovation like seen in London mansion blocks. All flats have gas heating. Costs are then dramatically cut for the electrical installations giving full protection.

AFDDs may drop dramatically in price, but far from that yet. The drop in the price is only opinion.
 
Last edited:
I doubt anyone renovating a mansion block in London will be considering the savings from omitting a few AFDDs in fact the wiring in such an installation is likely to be complex, no expense spared.
 
Adding another AFDD at ÂŁ150, is not an option, as costs spiral.

The exercise is to get full AFDD protection in a flat meeting regs at minimal cost.
 
I doubt anyone renovating a mansion block in London will be considering the savings from omitting a few AFDDs in fact the wiring in such an installation is likely to be complex, no expense spared.
I see no complexity in the wiring.

1. Heavy appliance sockets cable back to CU.
2. General sockets cable back to CU.
3. Lighting cable back to CU.
4. Cooker cable back to CU.
 
Last edited:
Status
Not open for further replies.

Reply to Cheap AFDD implementation in flats. in the Electrical Engineering Chat area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Replies
25
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top