The 2391 practical assessment
Before you start!!!
1. Ask for previous test results
Functional test
1. test 1 way light switch
2. test 2 way light switch
3. test dimmer light switch
4. test 3 phase socket with phase rotation tester (indicator lamp type or rotating disc type)
5. confirm operation of circuit breakers and main isolators
Earth fault loop impedance
1. test all sockets at single phase board and three phase board confirm polarity and function of sockets
RCD testing
1. draw a table to record results
2. make sure to test on both sides of negative and positive sides of supply
3. test via one socket at the three phase board and the other at the single phase board
4. record the highest result for both the 1x and 5x
Open covers to three phase board
Prospective fault current
1. check condition of instrument
2. isolate the installation
3. using a three lead tester set instrument to 20 ka, PSC
4. apply probes to incoming neutral conductors the earth lead also connect to the neutral conductor, then safe working practice safer to connect to the incoming L1 last
5. take note of the result
6. apply probes to incoming neutral conductors the earth lead also connect to the neutral conductor, then L2
7. take note of the result
8. apply probes to incoming neutral conductors the earth lead also connect to the neutral conductor, then L3
9. take note of the result
10. take note of highest result
11. for prospective fault current take highest reading then multiply it by 2
12. check the rating on protective devices for breaking capacity
Open cover to single phase board
1. (having already checked the instrument no need to recheck it)
2. using a three lead instrument connect to incoming neutral the earth lead to the neutral then connect to incoming line supply conductor
3. prospective earth fault current as above but the earth lead connects to the main earth terminal
4. record result the highest of the two results that is your PFC
Before you start!!!
1. Ask for previous test results
Functional test
1. test 1 way light switch
2. test 2 way light switch
3. test dimmer light switch
4. test 3 phase socket with phase rotation tester (indicator lamp type or rotating disc type)
5. confirm operation of circuit breakers and main isolators
Earth fault loop impedance
1. test all sockets at single phase board and three phase board confirm polarity and function of sockets
RCD testing
1. draw a table to record results
2. make sure to test on both sides of negative and positive sides of supply
3. test via one socket at the three phase board and the other at the single phase board
4. record the highest result for both the 1x and 5x
Open covers to three phase board
Prospective fault current
1. check condition of instrument
2. isolate the installation
3. using a three lead tester set instrument to 20 ka, PSC
4. apply probes to incoming neutral conductors the earth lead also connect to the neutral conductor, then safe working practice safer to connect to the incoming L1 last
5. take note of the result
6. apply probes to incoming neutral conductors the earth lead also connect to the neutral conductor, then L2
7. take note of the result
8. apply probes to incoming neutral conductors the earth lead also connect to the neutral conductor, then L3
9. take note of the result
10. take note of highest result
11. for prospective fault current take highest reading then multiply it by 2
12. check the rating on protective devices for breaking capacity
Open cover to single phase board
1. (having already checked the instrument no need to recheck it)
2. using a three lead instrument connect to incoming neutral the earth lead to the neutral then connect to incoming line supply conductor
3. prospective earth fault current as above but the earth lead connects to the main earth terminal
4. record result the highest of the two results that is your PFC