What is the reasoning behind this? I'd have gone for 2x rings with the heaters on FCUs.Don't want the heaters hard wired due to it being a sports hall.
Think of the amount of callouts if you fitted these heaters on a 13 A fcuWhat is the reasoning behind this? I'd have gone for 2x rings with the heaters on FCUs.
If it's only going to be temporary a diesel or propane heater will chuck out a lot more heat than small fan heaters.
Or is it a trick question, ie you don't need heating at the moment?
Maybe, but 3000/240 = 12.5, 240v being more like what you actually get in the UK. 2x2.5mm are easier to terminate than 2x4mm. If the ring only consisted of FCUs supplying heaters then that would make it a "dedicated circuit" would it not?Think of the amount of callouts if you fitted these heaters on a 13 A fcu
3000W /230 =13.04A mps wouldn't take long to blow those would it, an why Ring Final, what's the point? plus the BS 7671 RECOMENDS that a fixed load of plus 2KW would be better on a dedicated circuit.
It could well do until some idiot come along and sees it's RFC and starts adding 13Amp socket all over the shop, not realising it's a dedicated circuit for heaters.Maybe, but 3000/240 = 12.5, 240v being more like what you actually get in the UK. 2x2.5mm are easier to terminate than 2x4mm. If the ring only consisted of FCUs supplying heaters then that would make it a "dedicated circuit" would it not?
Maybe, but 3000/240 = 12.5, 240v being more like what you actually get in the UK. 2x2.5mm are easier to terminate than 2x4mm. If the ring only consisted of FCUs supplying heaters then that would make it a "dedicated circuit" would it not?
HT niceHmmm good point, thanks. Remind me, what reg is it that says we're allowed to design by 240v again? I forget.
They would take a bit of 'blowing' but, from what I've seen, the plug/sockets would be giving a fair bit of heat off.Think of the amount of callouts if you fitted these heaters on a 13 A fcu
3000W /230 =13.04A mps wouldn't take long to blow those would it, an why Ring Final, what's the point? plus the BS 7671 RECOMENDS that a fixed load of plus 2KW would be better on a dedicated circuit.
They would take a bit of 'blowing' but, from what I've seen, the plug/sockets would be giving a fair bit of heat off.
One place has one on a 4mm radial (a couple of other sockets involved) no fuse problems but a lot of heat at the plug....it worries them a bit.
What surprises me about these 3kw heaters is that some do come with a 13amp plug top fitted.
If you're looking to future additions, maybe 4mm2, 20amp DP switches.
Perhaps you'd care to explain that one then Pete?Nice
HT nice
I am mate, but I would prefer it if the suggestions complied with the rule book.I thought you were asking for suggestions.