Hello. I need advice about choosing MCB for cable overload protection.
I'm using BS7671:2008 Requirements for Electrical Installations.
Reg 433.1.1 has 3 requirements:
1. Ib <= In
2. In <= Iz
3. 1.45Iz >= I2
I don't understand reason of 1.45Iz >= I2.
And I think this requirements are not enough to cable overload protection.
Example.
Ib=9A
In=10A, I2=1.45In (MCB to BS EN 60898)
Iz=11A
1. Ib < In success (just for circuit design)
2. In < Iz success
3. 1.45Iz > I2 success
One day current in circuit (I) increases to 14A. CB will not operate because I < I2 or 14A < 14,5A. Cable will be overloaded because I > Iz or 14A > 11A.
Sorry for my english.