Hi all

I'm doing a kitchen rewire and in kitchen client has also had a new water cylinder installed. It is a Main unvented direct 170L. I have been trying to get through to customer support but is non existent. I have not wired many new circuits for water heaters and am a bit confused with the power ratings of it, so what size breakers and cable to use and also does it require two seperate supplies. As stated not great deal of experience with these so any point in right direction appreciated. I've included the manual and power ratings sticker. Thanks
 

Attachments

  • Main_Unvented_Direct_Indirect_36005994_issue_09.pdf
    1.9 MB · Views: 89
  • [ElectriciansForums.net] Circuit design for this water heater?
    IMG-20210108-WA0000.jpg
    134.6 KB · Views: 50
SOme things to clarify please:

1. Is it a direct tank ie: just heated by IH? The clue is whether or not there are flanges to connect boiler water supply and return to an internal heat exchanger.

2. It appears to me from the image - of the actual tank at site? - that it actually has two IHs - top and bottom which would be used normally for off-peak/full tank/bath heating and boost for top-up/sink heating.

3. Each element is 3kW with there own integral 'stat and safety cutout.

4. Is the site 'all electric'?

5. Ask the client if they are interested in wifi/phone app control of the two IHs which would allow the switching and time control to be out of sight and conveniently controlled by their phone.
Thanks Marconi

When you say IH I assume you immersion heaters? It is described as Direct so think yes heating is just achieve through the electrical immersion heaters.

3. Yes the thermostats incorporate their own cut out

4. It is an all electric site

5. Customer doesn't require wifi
 

Reply to Circuit design for this water heater? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
267
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top