C

Chris Ward

Can anyone shed any light on this for me.

Im putting in a supply to an outbuilding to supply a 13a water heater & 3a light, but picking a socket up on the way. Im wiring it in 4.0mm pvc twin cable from the DB, then 4.0mm 3core armoured outside. There is a DP switch incorporated near the DB in order to isolate the outhouse power from inside. The route the circuit will take is this:

(-> = Cable between)

(main building)DB1 -> 32a RCBO -> 32a DP Switch -> (goes outside) Outdoor twin socket -> (into outhouse) Un Switched FCU to supply water heater (13a fuse) -> Switched FCU for lighting (3a Fuse)

Im pretty sure this meets requirements for 433.1 Radial final circuit. Anyone got any input?
 
Seems pretty good to me, should the water heater not have a double pole isolation close at hand - you can get DP switched FCUs.
 
sounds good to me. make sure the SWA is properly glanded, the armor earthed at the supply end. might be an idea to fit a double metalclad socket in the outbuilding to gland the SWA. then metalclad FCUs.
 
Armoured will be glanded accordingly & armourings earthed, and the FCU for the water heater is now a DP switched unit. Thanks for that input, well spotted.

I had someone query the double socket fed direct from the 32a supply which cast a seed of doubt hence the post. But as we know the socket is limited to what can be plugged in.
 
Armoured will be glanded accordingly & armourings earthed, and the FCU for the water heater is now a DP switched unit. Thanks for that input, well spotted.

I had someone query the double socket fed direct from the 32a supply which cast a seed of doubt hence the post. But as we know the socket is limited to what can be plugged in.

not a problem. if you think about it, a " standard " ring final has sockets direct off a 32A supply, albeit wired in 2.5mm x2, ( for a ring final ) THE 32a MCB protects the cable, whether it be 2 x 2.5mm in a ring, or 4mm in a radial.
 

Reply to Circuit design - Outdoor radial in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Yes… as long as the initial radial circuit is designed properly regarding OCPD, cable size and rcd protection.
Replies
1
Views
715
  • Question
Why aren't you asking them?
Replies
5
Views
784
The 3A fuse is there to protect the current lighting. For additional power you connect from the non protected 3A fuse side.
Replies
1
Views
459
  • Question
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
Replies
2
Views
413
loz2754
L
  • Question
Great idea, thank you mate :)
2
Replies
38
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks