Scenario:
Small 2 bed terraced house. Ze 0.70 ohms on a TNS. One RFC ,PD 32amp type B. RCD protected.
Outdoor socket and lighting required in small rear garden.
Spur from kitchen socket to take power outside for one IP66 double socket and from there to 3 lights via FCU IP66 (3 amps max for lighting) Wired in 2.5mm three core SWA. Last part of lighting wired in flex.
I am after advice on VD calcs. I am scratching my head re Ib. The PD at the origin is rated 32 amps, it is fused down to 13 amp as the spur and then down again to 3 amps for the lighting. Its one radial circuit from the RFC to the lighting points.
I am after advice on Ib and if it's 3% or 5% as its a RFC and not a lighting circuit or as a radial is it worked out with both?? There are lights on it but fused down.
This is how this is to be done. This will not be taken from a spare way in the CU.
Brain ache with the calcs here though!
I like to understand everything you see.
Thanks
PP
Scenario:
Small 2 bed terraced house. Ze 0.70 ohms on a TNS. One RFC ,PD 32amp type B. RCD protected.
Outdoor socket and lighting required in small rear garden.
Spur from kitchen socket to take power outside for one IP66 double socket and from there to 3 lights via FCU IP66 (3 amps max for lighting) Wired in 2.5mm three core SWA. Last part of lighting wired in flex.
I am after advice on VD calcs. I am scratching my head re Ib. The PD at the origin is rated 32 amps, it is fused down to 13 amp as the spur and then down again to 3 amps for the lighting. Its one radial circuit from the RFC to the lighting points.
I am after advice on Ib and if it's 3% or 5% as its a RFC and not a lighting circuit or as a radial is it worked out with both?? There are lights on it but fused down.
This is how this is to be done. This will not be taken from a spare way in the CU.
Brain ache with the calcs here though!
I like to understand everything you see.
Thanks
PP