Socket circuit layout for rewire. I have changed the kitchen ring to 2x 20A radials. Smokes are on the lighting circuit, as it is less likely that this circuit will be isolated than an individual MCB.
Any suggestions, changes or additions welcomed. Has anything been overlooked.
Living Room - 20A Radial - 2.5mm - 3 Double Sockets
Dining Room & Hall - 20A Radial 2.5mm - 5 Double Socket
Bed1 & Bed2 - 20A Radial -2.5mm - 6 Double Sockets
Bed3 & Landing - 20A Radial -2.5mm - 4 Double Sockets
Kitchen Left - 20A Radial 2.5mm 2 Double plus Washing machine & Dishwasher
Kitchen Right - 20A Radial 2.5mm 2 Double plus Tumble Dryer
Freezer - 2.5mm 16A
Oven & Hob - 32A - 6mm
Outside Power - 20A - For future use
Lighting Upstairs - 6A 1.5mm- 5 Lights
Lighting Downstairs 6A 1.5mm- 5 Lights plus porch light plus smokes
All will fit into a 12way Hager CU. Installation method mixed, through joints, and in cable in conduit on a wall.
Any suggestions, changes or additions welcomed. Has anything been overlooked.
Living Room - 20A Radial - 2.5mm - 3 Double Sockets
Dining Room & Hall - 20A Radial 2.5mm - 5 Double Socket
Bed1 & Bed2 - 20A Radial -2.5mm - 6 Double Sockets
Bed3 & Landing - 20A Radial -2.5mm - 4 Double Sockets
Kitchen Left - 20A Radial 2.5mm 2 Double plus Washing machine & Dishwasher
Kitchen Right - 20A Radial 2.5mm 2 Double plus Tumble Dryer
Freezer - 2.5mm 16A
Oven & Hob - 32A - 6mm
Outside Power - 20A - For future use
Lighting Upstairs - 6A 1.5mm- 5 Lights
Lighting Downstairs 6A 1.5mm- 5 Lights plus porch light plus smokes
All will fit into a 12way Hager CU. Installation method mixed, through joints, and in cable in conduit on a wall.