could someone give me some help calculating a circuit resistance for a single phase circuit as it would be entered on a minor works cert if tested?
the circuit in question is a supply from a 2.5mm T&E 30m long going to fused spur then into 1.5 T&E 15m Long.
1st is the calculation done as two seperate calcs one for each cable size or just for the smaller cable?
also if i have a Ze of 0.8 how would i do the working out for the correct r1 + r2 for this circuit?
i think i have one over too much information and confused myself!!!!!
Are you talking about insulation resistance or r1 + r2? r1 + r2 should be taken from direct measurement or do a zs test and subtract ze to get r1 + r2
Is it a tns? can you take a direct measurement of r1 + r2?
zs = ze + r1 +r2
the measurement on my megger for r1 + r2 is coming up as 0.22 and the Zs reading is 0.6 can this be right or am i missing something here?
Sounds like parallel paths try disconnecting your bonding and doing zs again
Your ze is definately 0.8? is it a tns system?
is this measurement wrong then? what should the R1 + R2 compared to Zs 0.6 or vice versa Be!! im def confused now if i disconnect bonding and put that on a minor works certificate wont this not be incorrect readings for circuit being tested once bonding reconnected and put into service
Like i said before it should be zs = ze + r1 + r2, sorry bud if you don't know how to work these out you should'nt be doing the work anyway
Whilst Zs can be measured or calculated I don't believe you are allowed to subtract your Ze from Zs to give you (R1+R2). Don't forget parallel paths would be included.
Someone also mentioned disconnecting bonding. This should never be done on a live installation - as such you cannot measure Zs with an EFLI tester with the bonding disconnected.
zs=ze+(R1+R2) you can use this to calculate for zs but not for (R1+R2)
Sorry guys my mistake, i personally always measure everything anyway so never do the calculations to work the stuff out i just know the relationship between them all, its been a long week and my head is fried:D
Reply to circuit resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
6K