Pretty much as the title says - can anyone point me in the direction of guidance what distance I should allow between under floor heating and 2 x cables to an island in a new kitchen.

Thanks
 
Overall installing cables above underfloor heating is not a good idea. Installing them in ducting under the heat mat and under the heat mat floor insulation is a much better idea. However this does not seem to be an option in your case.
The maximum surface temperature for underfloor heating is about 35°C so a cable should be able to withstand that indefinitely, you would just need to derate the cable for the ambient temperature, however removing some of the floor to get the cables closer to the heat source does not sound good; would it be possible to overlay another floor surface and allow ventilation to the cables.
 
^^ I think you misunderstood my ill thought out response!

So laying the cables in a channel cut in the floor directly attached to the floor is OK then? (with the under floor heating above them..)
 
Maybe cut a channel in the floor (or perhaps have the builder cut the channel), and put the cables in flexi conduit in this channel. And have the channel deep enough so there is a significant gap before the heating pipes cross the cable (that gets filled in). But I guess it depends on the floor thickness, cutting the channel might well cut into the insulation below anyway!
 
^^ I think you misunderstood my ill thought out response!

So laying the cables in a channel cut in the floor directly attached to the floor is OK then? (with the under floor heating above them..)
Yes, I misunderstood and did not read the title of the thread.:sob:
So long as the cables are well below the level of the heating then they should be fine.
If there is no insulation for the heating then they will be wasting a lot of heat warming the ground below, but presumably it has been fine for 40 years, and I might think about putting insulation above (but not on) the cables to limit thermal conductance down to the cables. Ducting or conduit helps (a bit) if you ever have to remove the cables at a later date.
 

Reply to Circuits to kitchen island under (wet) under floor heating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
685
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top