Had a look at a job today which involves some additional sockets to the ring and a FCU.
As it's protected by a 3036 I was looking at providing an RCD in separate enclosure adjacent to the existing metal clad CU.
Also the DNO/metering co have been in recently and installed a new meter and 100A cutout (tails are 16mmsq) and the proper spiral spring clip earth connection to the incoming cable's lead sheath... but between the new MET and the CU the earthing conductor is a pair of approx 6mmsq green insulated wires, so am I right in thinking that's going to need upgrading to 16mmsq.
MPBCs are 10mmsq to gas and water, so no problem there.
Regarding the CU, I believe the 3036 types have relatively low breaking capacities - is there reference data available for them so I can see what spec the setup is?
I haven't done any PFC tests yet, but did do a quick Zs at a socket at the back of the house that I'd be doing some of the work from and it was very low at 0.31 Ohm so I'm expecting Ze to be 0.1 or less, with PFC in the region of 2.5kA
If this is the case, am i right in thinking the work can't be done without a board upgrade too?
Thanks,
Simon.
As it's protected by a 3036 I was looking at providing an RCD in separate enclosure adjacent to the existing metal clad CU.
Also the DNO/metering co have been in recently and installed a new meter and 100A cutout (tails are 16mmsq) and the proper spiral spring clip earth connection to the incoming cable's lead sheath... but between the new MET and the CU the earthing conductor is a pair of approx 6mmsq green insulated wires, so am I right in thinking that's going to need upgrading to 16mmsq.
MPBCs are 10mmsq to gas and water, so no problem there.
Regarding the CU, I believe the 3036 types have relatively low breaking capacities - is there reference data available for them so I can see what spec the setup is?
I haven't done any PFC tests yet, but did do a quick Zs at a socket at the back of the house that I'd be doing some of the work from and it was very low at 0.31 Ohm so I'm expecting Ze to be 0.1 or less, with PFC in the region of 2.5kA
If this is the case, am i right in thinking the work can't be done without a board upgrade too?
Thanks,
Simon.