Had a look at a job today which involves some additional sockets to the ring and a FCU.
As it's protected by a 3036 I was looking at providing an RCD in separate enclosure adjacent to the existing metal clad CU.
Also the DNO/metering co have been in recently and installed a new meter and 100A cutout (tails are 16mmsq) and the proper spiral spring clip earth connection to the incoming cable's lead sheath... but between the new MET and the CU the earthing conductor is a pair of approx 6mmsq green insulated wires, so am I right in thinking that's going to need upgrading to 16mmsq.

MPBCs are 10mmsq to gas and water, so no problem there.

Regarding the CU, I believe the 3036 types have relatively low breaking capacities - is there reference data available for them so I can see what spec the setup is?
I haven't done any PFC tests yet, but did do a quick Zs at a socket at the back of the house that I'd be doing some of the work from and it was very low at 0.31 Ohm so I'm expecting Ze to be 0.1 or less, with PFC in the region of 2.5kA
If this is the case, am i right in thinking the work can't be done without a board upgrade too?

Thanks,

Simon.
 
Last edited by a moderator:
I would say upgrade the main earth to a 16mm is definitely something that needs doing. An RCD in a separate enclosure will be fine. 3036 fuses are rated at 1kA from memory, this doesn't necessarily mean they need upgrading due to the main fuse being rated at 33kA however i tend to bung a 60898 retrofit MCB as a matter of course. Can't see the CU needs upgrading unless there is signs of damage though this would be entirely different if it was a old timber Wylex unit.
 
And so yet again we tend to ignore Reg Reg 543.1.1 espicially as if there is a spring clip onto a sheath I would imagine that this is a TN-S earthing arrangement.

The low Zs is not the sole indication you have a low Ze, if this is a TN-S system I would be amazed if you got a Ze of 0.1. Your low Zs could be the result of parallel path.
 

Reply to Clarification on addition/alteration to ring protected by BS3036 fuse in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top