hillbillie

How do you do an earth bond test for these? I have re read the IEE code of practice on this but I can't find an answer apart form: "...can give misleading results"

For example a class 1, totally plastic vacuum cleaner, at least on the outside (it has tiny metal screws not screwed into earthed metal). If there is nowhere to stick your lead can it be tested? Should I just do a visual and the insulation resistance test?
 
There's sometimes a little hole where you can poke your probe :D.
The 'by the book' answer would be to contact the manufacturer to find out how it's supposed to be tested, but personally I would just do the other inspections and tests.
 
Also think about AC adaptors or power supplies, some of which have no earth connected - even at ther output terminal - yet are constructed and fed with a dedicated IEC power cord.
In this case the earthed power cord is used to provide an earth for the correct fuctioning of the internal electronics and not to provide a CPC.

In this instance Adaptor is tested as Class II and power cord separately as IEC (extenion lead) and a note made to that effect.
 

Reply to class 1 equipment with no exposed earthed metal in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
494
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top