question my friend just phoned me hes a spark in industrial back ground any way hes just changed his consumer unit to a dual rcd board he seems to think the rcbo wont trip if he has a fault cos it has no earth but am i right in telling him which i think i am that it will trip as soon as it detects an in balance regardles of earth or no earth
Does the RCBO only feed class 2 fittings?
An imbalance means that somewhere current is going to earth, so on his class 2 fittings this will never be the case. Has he got earth cont at furthest point on circuit?
am i right in telling him that it will trip as soon as it detects an in balance regardles of earth or no earth
I would say you are (between Line & Neutral)
and...
You don't actually need a physical cpc present, eg a fitting might be damp and current is leaking away into the fabric of the building.
Right I see. Just read your post again and noticed you had actually said that.
Also just noticed Archy has added to his post what I was about to add regards leakage into the building structure and obviously nail or screw into cable then through said person putting nail or screw in, possibly!
Reply to class 2 lights on rcbo in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks for your reply. You are quite right, I’ve taken one down this morning and the cable is twin & earth but the earth has been cut right back...
And exciting when that Hager AFDD finally tripped 😂